I am thinking about writing a proposal to delete this article. I have only seen inspectors use this when they want something their way. This gives carte blanc authority to an inspector to basically fail a compliant install. What good is that. If the conductors and equipment are listed equipment then why should the authority having jurisdiction have the authority to turn it down.
Feed back please--- I realize it probably will not get accepted but I am not happy with its interpretation. Maybe there is a reason for this article but I don't see it-- enlighten me.
Feed back please--- I realize it probably will not get accepted but I am not happy with its interpretation. Maybe there is a reason for this article but I don't see it-- enlighten me.
110.2 Approval. The conductors and equipment required or
permitted by this Code shall be acceptable only if approved.
Informational Note: See 90.7, Examination of Equipment
for Safety, and 110.3, Examination, Identification, Installation,
and Use of Equipment. See definitions of Approved,
Identified, Labeled, and Listed.