M. D. said:In Mass this is expressed in rule #3 .My question is How do we add without increasing the magnitude:-?
M. D. said:Rule 3. Additions or modifications to an existing installation shall be made in accordance with this Code without bringing the remaining part of the installation into compliance with the requirements of this Code. The installation shall not create a violation of this Code, nor shall it increase the magnitude of an existing violation.
Let me run a scenerio by you and you tell me how this rule 3 would apply.
Existing is a service and a subpanel. . Subpanel feed without metal conduit and without an equipment grounding conductor. . Ground bar and subpanel housing are either floating or are bonded to the neutral. . No, let's change that and say that there is no ground bar, all circuit grounds in the subpanel are on the neutral bar and we'll say the panerl housing is not bonded to anything.
Your scope of work is to add a circuit in an addition. . Does rule 3 allow you to run your HR back to that subpanel without fixing the subpanel ? . If yes, where do you land your equipment ground wire from your new homerun.
David