dw85745:

Some basic information to work from.

A single phase motor fed from a single phase source will not self start mechanical rotation. It will just sit nearly still, but you will feel or hear it vibrate. It can be started by some external applied rotation, a rope and pullly, or something else to momentarily drive the rotor.

To electrically start a single phase motor you need some electrical scheme to produce some limited sort of rotating magnetic field. Thus, at least for starting purposes the motor needs to be at least a 2 phase motor. There are various ways to accomplish this.

The circuit shown by ptonsparky consisted of two phase shifting circuits. One circuit is a capacitor and another coil that is not the main power coil. This circuit is present both during starting, and running. The second circuit adds more capacitance in parallel with the first capacitor ( more starting torque ) just during starting ( in some fashion with some time delay to opening ) .

I don't believe this normally closed contact in series with the starting capacitor is voltage controlled from something relating to starting voltage unless the relay contact also has a time delay function.

.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
221110-2100 EDT

dw85745:

Some basic information to work from.

A single phase motor fed from a single phase source will not self start mechanical rotation. It will just sit nearly still, but you will feel or hear it vibrate. It can be started by some external applied rotation, a rope and pullly, or something else to momentarily drive the rotor.

To electrically start a single phase motor you need some electrical scheme to produce some limited sort of rotating magnetic field. Thus, at least for starting purposes the motor needs to be at least a 2 phase motor. There are various ways to accomplish this.

The circuit shown by ptonsparky consisted of two phase shifting circuits. One circuit is a capacitor and another coil that is not the main power coil. This circuit is present both during starting, and running. The second circuit adds more capacitance in parallel with the first capacitor ( more starting torque ) just during starting ( in some fashion with some time delay to opening ) .

I don't believe this normally closed contact in series with the starting capacitor is voltage controlled from something relating to starting voltage unless the relay contact also has a time delay function.

.
The delay function is in how long it takes for the cemf to build up. (I think that is the term). The potential relay is very common in well motors, air conditioning, and refrigeration. I've also seen it on older higher HP table saws. Delta brand IIRC.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
221111=0016

ptonsparky:

See my thread
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
221111=0016

ptonsparky:

See my thread
Okay, I'll look it over again.

Not sure how it relates to the common use of potential relays in single phase motors and this thread.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Ok. Got it.

Nice to see how little the voltage must increase to open the contacts. It's no wonder those relays may be position sensitive.

I replaced the old mechanical potential relay in the above table saw with a solid state. The originals were no longer available. It took some effort to adjust the time of drop out.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
221111-1530 EST

I don't know why one would use a voltage sensitive relay to control the dropout point for an induction motor start winding unless the voltage to that relay was from a generator on the motor shaft where the output voltage was proportional to motor speed. Motor current is easily available and does a good job of indicating when the motor is up to a reasonable speed.

.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
221111-1530 EST

I don't know why one would use a voltage sensitive relay to control the dropout point for an induction motor start winding unless the voltage to that relay was from a generator on the motor shaft where the output voltage was proportional to motor speed. Motor current is easily available and does a good job of indicating when the motor is up to a reasonable speed.

.
Because it works?
We both know I won't be able to explain it.
Maybe one of the motor guys will jump in.
 

TwoBlocked

Senior Member
Location
Bradford County, PA
Occupation
Industrial Electrician
Here's how I see it: Any motor when starting draws a lot of current. That current goes down as the motor comes up to speed. With the start winding in series with the capacitor(s), the voltage is divided between the two. At first the start winding has a low impedance (inductive reactance) while the capacitor(s) have a higher impedance (capacitive reactance). Sooooo, there is a greater voltage drop across the capacitor(s) and less across the start winding. The voltage across the potential relay is the same voltage across the start winding because they are connected in parallel. The voltage across the potential relay is not high enough to energize the relay until some point as the motor comes up to speed and the current decreases. At that point the voltage is divided more evenly between the start winding and the capacitor. There is then sufficient voltage across the potential relay to energize and for the contacts to switch state.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
221111-1725 EST

TwoBlocked:

Get yourself a memory scope, a current transformer, and a voltage probe. Add to this a motor speed sensor proportional to motor shaft speed. Then also someway to sync the scope to turn on time of the motor. Observe your waveforms, and compare those observation with your verbal description.

.
 

TwoBlocked

Senior Member
Location
Bradford County, PA
Occupation
Industrial Electrician
221111-1725 EST

TwoBlocked:

Get yourself a memory scope, a current transformer, and a voltage probe. Add to this a motor speed sensor proportional to motor shaft speed. Then also someway to sync the scope to turn on time of the motor. Observe your waveforms, and compare those observation with your verbal description.

.
I'll leave that to you.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
221112-0933 EST

TwoBlocked:

Yes, it is quite interesting how the capacitor fed coil has a substantial voltage increase when the motor reaches near full speed. Certainly enough to be detected. I did not try to analyze, observe, how this varies with supply voltage, or motor load.

.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Thanks both for replies.
petersonra:
I've been hesitant to take a voltage across the contacts as IMHO, that would be like trying to take the voltage on a wire. Am I wrong on this?
I have a sketch, will try and see if I can scan in and post. Late here so tomorrow.
The better analogy is that the closed contacts are like a wire, so no voltage.
The open contacts are like a cut wire, so the voltage will depend on what is connected to either side.
 