Hi all, been a while, but I was researching MWBC and this thread came up.
A few posts back, someone was discussing amps (and thus 'poor' connection watts) per device per strap etc...
If one broke the brass side 'jumper', wired a 20 amp MWBC, and measured current - I believe there would still be a max of 20 amps (but at 240 volts) at any point. Think matched loads, neutral flow is '0', and the 20 goes through 1 load, the neutral 'jumper', and then through the other load. A marginal connection could 'heat' a few ohms at 20 amps for X watts, and then again at another connection, etc, maybe 6 times.
The other scenario - 2 separate circuits, both 'jumpers' broken out - could be 20 amps on each device with the 'same' 120's or 2 different 120's (Potentially 8 poor connections?) I have to think that if that was not allowed, there would be no reason to have a breakable jumper on the neutral. The breakable jumper seems to imply that the total device can handle the heat from 20 amps twice - either from a MWBC, or two circuits.
Trying to help...
Now to my interest...
I'm trying to understand practicality of the previous rule of tied breakers for MWBC if landed on same strap.
I see it explained as for worker safety.
Seems that it assumes a worker will not see the broken 'jumper' before before pulling out the strap (but after turning off only breaker #1).
Is that really any different than a double switch (single strap) with 2 different feeds? Or a Cmas light receptacle (1/2 room circuit, other half global switched circuit, but not MWBC's)
Is there a better reason?
THX