DaveTap
Senior Member
- Location
- Currently Flowery Branch, GA
I have to upgrade an existing 100 amp residential panel in NW Chicago suburbs to 200 amps and I'd really like to use the existing 1-1/4" service riser because it is buried inside of the existing barn style roof.
Table 310.15(B)(6) says the 200 amp service could be 2/0 copper and Table C.8(A) allows three 2/0 Compact Conductors in 1-1/4" RMC.
Local inspector says it has to be 2" RMC because ComEd requires it but ComEd says there is no such requirement.
Is there anywhere in the code that states this service must be a 2" conduit or is it acceptable to re-use the existing 1-1/4" drop?
Table 310.15(B)(6) says the 200 amp service could be 2/0 copper and Table C.8(A) allows three 2/0 Compact Conductors in 1-1/4" RMC.
Local inspector says it has to be 2" RMC because ComEd requires it but ComEd says there is no such requirement.
Is there anywhere in the code that states this service must be a 2" conduit or is it acceptable to re-use the existing 1-1/4" drop?