Found this on another site, what do you guys think
Equipment grounding conductors are selected from Table 250.122 based on the size of the overcurrent device protecting the circuit. If the ungrounded conductors of the circuit are increased to allow for voltage drop, or because of manufacturer?s instructions, the equipment grounding conductor must be increased in size by the same proportion that the ungrounded conductors have been increased. For example, if the size of the ungrounded conductors is increased by 25%, the size of the equipment grounding conductor must be increased by 25%.
The language in the 2011 NEC was not clear about why the ungrounded conductors would be increased in size. Ungrounded conductors are often increased in size because when more than 3 current-carrying conductors are in conduit, or used in a hot ambient temperature, the conductor cannot perform at the same ampacity. The intent of this section was not to require an increase in the size of the equipment grounding conductor under these conditions of use for the ungrounded conductors.
The 2014 NEC clears this up by saying the equipment grounding conductor needs to be increased in size only if the ungrounded conductors are increased in size beyond what is needed for the ?sufficient ampacity for the intended installation.? In other words, if the ungrounded conductors are increased in size because there are more than 3 current-carrying conductors in conduit, or the ambient temperature is above 86?F, the equipment grounding conductor is not required to be increased in size.
In the 2011 NEC there was also confusion about what to do if the equipment grounding conductor was a metallic raceway. Was it necessary to increase the size of the raceway if the ungrounded conductors were increased in size? This was never intended, and the 2014 refers to ?wire-type? equipment grounding conductors as the only type of equipment grounding conductor that needs to be increased in size.