That's not the best explanation for him if he doesn't understand it.
Actually, that's a confusing explanation.
If he shuts off the 2p breaker feeding the unit he will read zero at the unit.
To the OP,
In very simple terms picture a 240v incandescent light bulb.
Power goes to the lamp on A phase through the filament and back on B phase to the panel.
2 different phases or "Legs" are in play in this scenario, thus both A and B phases or "Legs" are connected at the light bulb socket, you would read 240 volts at the socket, and, the bulb would be lit.
Now,
Picture taking the B phase return wire off of the 2 pole breaker at the panel.
The bulb goes out because it's lost it's 240v supply.
It is not designed to operate on only 120 volts.
In this scenario 120v travels from the panel on A phase to the socket "through the filament" and back on B phase to the panel, but you've taken the wire off of B phase at the panel.
Therefore, you've lost your 240v circuit and are dealing with only A phase from the panel through the filament and back to where you took it off.
If you take your meter and read the voltage at the socket you would read A phase only or 120v to ground on both the supply and return wires connected to the socket because you are reading through the filament on the bulb.
But,
You would read "Zero" between the 2 wires because B phase was disconnected and your taking a reading on only the A phase conductor by itself.