220 Circuit 50amp- EMT with Metalic Boxes. Grounding Confusion.

Status
Not open for further replies.

cc4digital

New User
Location
California, Riverside County
Occupation
Computer Programmer
I am working off a sub-panel that is not bonded and has its own ground that goes to a ground rod.(y)

I need clarification on how to ground the box without using a pigtail.:unsure:

This seems overkill, but maybe to avoid code issues at a later time. I am currently thinking of:
  1. Using 3/4" conduit- 50ft
  2. Run four wires, #6 THHN, Black, Red, Green, Bare Copper
  3. Hook Black, Red, and Green to Receptacle
  4. Hook Bare Copper to metallic boxes using a green ground screw
  5. Of course, then connect Bare Copper and Green to the Ground Bar at the Panel.
  6. Connect Black and Red to 220 50amp Breaker.

Thought or Comments?:oops:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
This site is designed for:
  • Electrical Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
This NEC® Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

Knowledge and the practical application of the National Electrical Code is an essential part of all electrical installations. If it's important for you to understand the National Electrical Code, then look no further.

To better help us serve you, please be sure to update your account details with your occupation field and location if you have not done so already. You can access your account details by clicking on your account name at the top right of the page when on the forums.
 
Status
Not open for further replies.
Top