3 apartments share a 2-inch conduit, 9 conductors total. Apartments are 120/208V single phase. A raceway is used as an equipment grounding conductor so there are no non-current carrying conductors in this raceway.
If all 3 apartments are upgraded to 100Amps, would it be legal to use (9) #2 THWN-2, 90 degrees C copper conductors in the shared 2-inch conduit?
This is how I did my calculation:
100A*83% = 83A as per 310.15(b)(7)
83A/70% = 118.6A wire required as per table 310.15(B)(3)(a) because there are 9 current carrying conductors in a raceway
Since 90 degrees wire is used, we derate from 90 degree column and the next size up to 118.6A is #2 wires
Is this correct?
If all 3 apartments are upgraded to 100Amps, would it be legal to use (9) #2 THWN-2, 90 degrees C copper conductors in the shared 2-inch conduit?
This is how I did my calculation:
100A*83% = 83A as per 310.15(b)(7)
83A/70% = 118.6A wire required as per table 310.15(B)(3)(a) because there are 9 current carrying conductors in a raceway
Since 90 degrees wire is used, we derate from 90 degree column and the next size up to 118.6A is #2 wires
Is this correct?