cwgreenelectric
Member
- Location
- Washington County Florida
- Occupation
- Contractor, Trade School Instructor
What are your thoughts?
I recently had a service call to check out dimming lights in a residence that recently had an addition ( converted a carport to a room).
During my survey I found a new 18kw electric tankless water heater. Every time it came on the voltage feeding the house dropped 30 volts. This was measured at the top of the meter. I had the customer contact the poco for repair. Customer indicated 2 weeks later that the problem was fixed.
A few days later I ran into a manager from the poco and asked what they found. She told me that they are tired of having to change transformers and service drops because customers are installing these high wattage electric appliances without first checking with them about service requirements and are likely going to start charging customers for the upgrades.
The house was mid 70s and probably 1 of 3 houses on the transformer. House had original 200a service and well within the 200a load calculation. Currently there are 5 houses on the service transformer.
How can the poco justify charging customers for upgrades to their system when the home is still well under load of the original service supply equipment?
I recently had a service call to check out dimming lights in a residence that recently had an addition ( converted a carport to a room).
During my survey I found a new 18kw electric tankless water heater. Every time it came on the voltage feeding the house dropped 30 volts. This was measured at the top of the meter. I had the customer contact the poco for repair. Customer indicated 2 weeks later that the problem was fixed.
A few days later I ran into a manager from the poco and asked what they found. She told me that they are tired of having to change transformers and service drops because customers are installing these high wattage electric appliances without first checking with them about service requirements and are likely going to start charging customers for the upgrades.
The house was mid 70s and probably 1 of 3 houses on the transformer. House had original 200a service and well within the 200a load calculation. Currently there are 5 houses on the service transformer.
How can the poco justify charging customers for upgrades to their system when the home is still well under load of the original service supply equipment?