I don't think they are supposed to be coordinated with. I think they are there solely in case one cable of a parallel set has a fault that needs clearing.How does thus compare to a typical OCPD? Your example is for a limiter to protect 500kcmil which is typically applied at roughly 380A. The TCC shows this limiter would carry roughly 2500A for10 sec before opening. This doesn't seem like it would be easy to coordinate with.
I can't imagine this would be a legal NEC install. Utility side only. I could see a utility not wanting to trip a whole service if just one cable faulted.
The code does not seem to allow for an ocpd that only opens one of the parallel conductors, plus there is the problem of the code not allowing for ocpd in parallel.