If i'm running multiple circuits on cable tray (may be not listed to be used as EGC) & i'm going to install conduits to fit all drops down <9 ft from cable tray to served panel, in case of having two or more conduits for one circuit does it need a separate EGC for each single conduit along the line from the upstream to downstream or one EGC is OK since it's just max 9 ft.