I was going through the 2014 code book to size a 400 amp underground service when I came to the conclusion that I might be able to use parallel 1/0s. Let explain and maybe someone could chime in when they find my mistake.
First the layout of the service: We are connecting to the utility transformer at the corner of the property. We are installing a 400 amp meter/main next to the transformer. Then the feeder goes 400ft in two 2 inch PVCs buried 4? deep to the foundation. We then go into the basement where there is a 400 amp disconnect. At the meter the feeders emerge in PVC out of the ground 4ft and at the house they extend into the basement in PVC 10ft. The calculated load for the house is 250 amps.
My first step was using 310.15(B)(7)(2). Which allows conductors with an ampacity of 83% of the feeder rating. In my case 322 amps for one conductor or 166 amps for parallel conductors.
Next I found the ambient adjustment correction factor for the ambient temp of the underground run which from what I could find was 55 degrees F. So the adjustment factor is 1.15. Since the amount of conductors that leave the 55 degree portion is 10ft or less at each end I feel 310.15(A)(2)Exception applies.
Next I went to Table 310.15(B)(16) and found that 1/0 THWN copper, after applying the temp correction, can handle 172.5 amps in the 75 degree C column.
Now I have never heard of this before so I?m thinking I have made a mistake by applying the ambient adjustment factor. But I can?t see where in the code book that would not allow me to use the correction factors.
When I asked the inspector he said that using the 83% residential adjustment does not allow me to take any other adjustments.
Am I mistaken or can I use 1/0 in this situation.
First the layout of the service: We are connecting to the utility transformer at the corner of the property. We are installing a 400 amp meter/main next to the transformer. Then the feeder goes 400ft in two 2 inch PVCs buried 4? deep to the foundation. We then go into the basement where there is a 400 amp disconnect. At the meter the feeders emerge in PVC out of the ground 4ft and at the house they extend into the basement in PVC 10ft. The calculated load for the house is 250 amps.
My first step was using 310.15(B)(7)(2). Which allows conductors with an ampacity of 83% of the feeder rating. In my case 322 amps for one conductor or 166 amps for parallel conductors.
Next I found the ambient adjustment correction factor for the ambient temp of the underground run which from what I could find was 55 degrees F. So the adjustment factor is 1.15. Since the amount of conductors that leave the 55 degree portion is 10ft or less at each end I feel 310.15(A)(2)Exception applies.
Next I went to Table 310.15(B)(16) and found that 1/0 THWN copper, after applying the temp correction, can handle 172.5 amps in the 75 degree C column.
Now I have never heard of this before so I?m thinking I have made a mistake by applying the ambient adjustment factor. But I can?t see where in the code book that would not allow me to use the correction factors.
When I asked the inspector he said that using the 83% residential adjustment does not allow me to take any other adjustments.
Am I mistaken or can I use 1/0 in this situation.