meternerd
Senior Member
- Location
- Athol, ID
- Occupation
- retired water & electric utility electrician, meter/relay tech
400A "K base" bolt in meters are long gone. No longer available from manufacturers. The CL320 "S base" meters are the replacement. I assume (but I can't prove it) that the 400A meters really were intended for 80% (320A) continuous duty. The utilities I worked for eliminated the K base meter by installing an S base adapter and installing a CL320 meter. Problem with the bolt in meters is that an exchange or disconnect required a service shutdown and a time consuming removal procedure. With the newer PPE requirements, it's much too troublesome as far as maintenance, testing, smart meter installation, etc. One manufacturer also made a CL320 three phase non-CT (self-contained) meter, but not many utilities allowed 'em. Don't know if they're even still available. We required CT's for anything over 200A three phase and any non-residential over 200A. Requests for 400A single phase services are supplied with 320A meters, even though the fees are identical to the older 400A services. Kinda off the subject, but manufacturers decided to make the CL320 meters with the same meter stabs as the CL200. That means the meter sockets are also the same dimensions, and there's nothing preventing the utility from installing a CL200 meter in a CL320 socket. Eventual meltdown is the result. "Smart meter" change-out contractors beware!:rant: