40a Single Pole Breaker

Moore21

Member
Location
Lancaster CA
Occupation
Electrician
I was working on a panel and they had a single pole 40a breaker in the panel. It was wired incorrectly so I asked the homeowner what it was for and he had no idea. I tried to trace it the best I could without opening walls, to no avail.

Does anyone have an idea of an appliance or other electrically powered device that would be 120v-40a?
 

retirede

Senior Member
Location
Illinois
I’m having a hard time visualizing how a single-pole breaker can be wired incorrectly. Can you give us more details?

Is the wire sized adequately? I could see a homeowner installing a larger breaker because it was tripping.

Answers to these may aid our wild speculation!
 

Moore21

Member
Location
Lancaster CA
Occupation
Electrician
I’m having a hard time visualizing how a single-pole breaker can be wired incorrectly. Can you give us more details?

Is the wire sized adequately? I could see a homeowner installing a larger breaker because it was tripping.

Answers to these may aid our wild speculation!
Turn the breaker off. Check freezers etc before you leave. Have customer call when he notices what's off.
Possibly an out building?
It's not currently in use. When I removed the deadfront They had a neutral(white) wire landed on the breaker and the black from that same cable was capped off. I'm not really trying to restore power to that circuit, so much as I was just curious to what it was meant to operate. I cannot think of anything that would need a single pole breaker that size.
But thank you for the input.
 

Moore21

Member
Location
Lancaster CA
Occupation
Electrician
I’m having a hard time visualizing how a single-pole breaker can be wired incorrectly. Can you give us more details?

Is the wire sized adequately? I could see a homeowner installing a larger breaker because it was tripping.

Answers to these may aid our wild speculation!
See other reply.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It would still be interesting to know if the wire was sized adequately for a 40A OCPD.

I wonder if the circuit was originally connected to a 2-pole breaker (240V load)?
It could be an electric range circuit that was converted to 120v for a gas range.

If so, the hot white wire could explain the "improperly-wired" comment.
 