i recently read an engineer's response to a third party report about an installation that he had designed. in the report it was noted that the #2 Cu grounding electrode conductor installed on a service that was fed with 3 parallel 500 kcm per phase was to small according to table 250.66 in the NEC. the engineer responded by saying that according to 250.66(a) the grounding electrode conductor doesn't have to be larger than #6Cu if it connected to a ground rod.
after looking at the referenced sections in the code, i have concluded that when 250.66(A) refers to "that portion of the conductor that is the sole connection to the grounding electrode...", it means that the part of the conductor that is in contact with the rod does not have to be larger than #6. the GEC itself must still comply with table 250.66.
how do you guys interpret this?
after looking at the referenced sections in the code, i have concluded that when 250.66(A) refers to "that portion of the conductor that is the sole connection to the grounding electrode...", it means that the part of the conductor that is in contact with the rod does not have to be larger than #6. the GEC itself must still comply with table 250.66.
how do you guys interpret this?