Is a run of EMT installed in a series of web joists without any fastening (aside from within 3' of each box) code compliant?
 

mcclary's electrical

Senior Member
Location
VA
There is a burrito on the line, and I've been elected referee of it's fate.

Is a run of EMT installed in a series of web joists without any fastening (aside from within 3' of each box) code compliant?

358.30 (b) permits this. I say it's legal as long as the webs are closer than 10 feet, you could only have two supports on an unlimited length
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Which way do I need to vote to get the burrito ?

According to the commentary and illustration in the handbook, you are compliant.
I guess the only argument would be if one considers bar joists to be "framing members"

I voted compliant
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
I said no, because to me, "...through framing members..." means, holes, not laying on top of framing members, but I may not be picturing it in my mind right either.

Have a picture?
 

480sparky

Senior Member
Location
Iowegia
I had no trouble understanding plain English but thanks for helping those in the corn fields out. :grin:


I think it's painfully obvious that I got it, too, Bob.


I was just making the correction for all those city-clickers out there.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I vote compliant. There's even a diagram of this in the handbook, and the handbook is gospel, right? :)
 

Smart $

Esteemed Member
Location
Ohio
... I guess the only argument would be if one considers bar joists to be "framing members"

...

I don't think there is any question as to bar joists or truss joists are framing members. I think what is more questionable is the size of "openings" and how much lateral movement they permit.

Yet given the current wording, I too voted compliant.
 

brentk

Member
Location
Minnesota
Apologize for using the 2005 for this, my 2008 book is not handy at the moment.

358.30 Securing and supporting. EMT shall be installed as a complete system in accordance with 300.18 and shall be securely fastened in place and supported in accordance with 358.30(A) AND (B).

(A) Securely Fastened. EMT shall be securely fastened in place every 10 ft. .....

(B) Supports.....

In my interpretation (B) is not to be used as an exception from the requirements of part (A).

I vote NO.
 

iwire

Moderator
Staff member
Location
Massachusetts
I don't think there is any question as to bar joists or truss joists are framing members. I think what is more questionable is the size of "openings" and how much lateral movement they permit.

Yet given the current wording, I too voted compliant.

I see it the same way.
 

Smart $

Esteemed Member
Location
Ohio
For all of you that are ready to eat your burrito, what about 300.11?
I believe 300.11 is subjective, subject to speculation, and seems to be written more for support via wire. Where it says "securely fastened in place, it expresses no maximum interval, so the within 3' of termination points satisfies that requirement.
 

480sparky

Senior Member
Location
Iowegia
I'm invoking Charlie's Rule on you! :cool:

The context of the word "series" was that of a collection, a set, a group. The question did not imply the web boards were in series with each other..........

I never applied the word 'series' to the framing itself, but rather the direction of the EMT in relationship to the direction of the framing.


...And you can buy one for me with all the trimmings. :)

Collect from the OP. I never offered any burritos.
 