Additional Service??

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
where do you group your(six or less) service disconnects? This sounds like they are located in each apartment.
They would be in each occupancy nearest the point of entrance of the sevice conductors. This would not work well in most appartment applicaitons unless you could install the panel on an outside wall, but is common in single story mulitple occupancy buidlings where the service conductors are run from the meters either along the outside wall to each occupancy or under the slab to each occupancy.
 