Another mobile home in distress. See photos. Meter and 100 breaker disconnect is located less than 30' from the MH. The MH "disconnect" is now a junction box, no ground (only 3 conductors) and the inside panel has the neutral & ground tie together and are bonded only to the frame of the MH and no rods/electrodes.
Because the disconnect at the meter is less than 30', can I legally for a mobile home use the inside panel as a main and bond it to the 2 rods and leave, after cleaning the junction box as it is now? The photo shows the inside Federal Pacific (oh, oh) that I plan to clean and organize as the bus looks in good condition. Another low income situation. Sorry for many question, but been new in WA, new with NEC 2014, new with WAC and doing MH with very little money is no fun.
In another note: if a regular person read all topics posted in the forum (thousands) that person will be super qualify for a Master License!
Because the disconnect at the meter is less than 30', can I legally for a mobile home use the inside panel as a main and bond it to the 2 rods and leave, after cleaning the junction box as it is now? The photo shows the inside Federal Pacific (oh, oh) that I plan to clean and organize as the bus looks in good condition. Another low income situation. Sorry for many question, but been new in WA, new with NEC 2014, new with WAC and doing MH with very little money is no fun.