Is this a legit use for metal conduit?
Is this a legit use for metal conduit? View attachment 5933
I don't necessary see a problem with the caulking, but is that conduit PVC? I can swear the connector going into the hub is a pvc connector.In that case I like the low voltage grounding the utility installer got in there.
And it wouldn't be the first time I've seen this done by the phone installers. Seen hundreds of places where the paint is not cleaned and 4-5 places where the installer just clamped it on a pvc conduit.
besides that phone bond would serve no use if that was PVC:happyno:
EMT? That might be a problem ....
EMT fittings have straight threads; hubs have tapered threads. The end result is that the EMT fittings won't go into hub far enough for a good connection - and the putty hides this.
I'm not sure I've seen electrical reducing bushings with wrench flats. Could that be a plumbing fitting?