I'd have to agree with you, and there are probably threaded studs under the caps.Hmmm, could it be this bold text near bottom left of label?
"Suitable for connection to utility interactive equipment ......Order subfeed lug kit CAT. NO. SR69064A"
i have used similar PanelWhat are these?
(black insulated bolts(?) in upper left, on main bus bars)
Newish Square D 200A combo meter/main
View attachment 2570697
... but this one doesnot have cover to protect the connection like this one has?
Sure looks like it.Hmmm, could it be this bold text near bottom left of label?
"Suitable for connection to utility interactive equipment ......Order subfeed lug kit CAT. NO. SR69064A"
Nice connection in your install photo!i have used similar Panel
SC3042M200PF but bottom fed, pretty handy for supply side connection. but this one doesnot have cover to protect the connection like this one has?
Only if Enphase has a meter based isolation device comparable to Tesla's Backup Switch, as the Microgrid Isolation Device has to be upstream (utility side) of both the BESS and the loads to be backed up.So it looks like I can backup the whole house with an Enphase battery system thru these terminals?
If you move all the load breakers to a different panel. I think it makes more sense for partial home backup with some loads not backed up.So it looks like I can backup the whole house with an Enphase battery system thru these terminals?
I appreciate the desire to only back up critical loads in a new sub panel (SP). More efficient.If you move all the load breakers to a different panel. I think it makes more sense for partial home backup with some loads not backed up.
The lugs get you around the 70A backfeed restriction if you have to apply the 120% rule. Not much more than that.
Seems there is another cover that has been removed, but at same time what is the point of the barriers on the main breaker lugs if there is no cover on these supply side tap lugs and an additional cover that provides barrier for all of them?i have used similar Panel
SC3042M200PF but bottom fed, pretty handy for supply side connection. but this one doesnot have cover to protect the connection like this one has?