5- 136 - (250-50): Reject
SUBMITTER: Noel Williams, Noel Williams Consulting
RECOMMENDATION: Add the following to the end of the
second paragraph:
"A grounding electrode conductor connecting to multiple made
electrodes as permitted in Section 250-52(c) or (d) shall be sized
according to Table 250-66. "
SUBSTANTIATION: According to the present rule, the
conductor to a single rod, pipe, or plate electrode need not be
larger than No. 6 copper (or No 4 aluminum). For a group of
made electrodes, the largest conductor required for any electrode
in the group is also No. 6 copper. Even where many such
electrodes are used as a grounding electrode system, the largest is
still No. 6. Therefore, where multiple made electrodes are used
to increase the overall contact area, the conductor is not required
to be increased under the present rule. This is inconsistent with
the reasoning behind Section 250-66(a). The rule as written is
not a problem when applied to concrete-encased electrodes or
ground rings, because even where multiple connections are made
they are all made to the same electrode(s).
PANEL ACTION: Reject.
PANEL STATEMENT: The panels intent is to permit the
specified size of grounding electrode conductors when connected
to single or multiple made electrodes.
NUMBER OF PANEL MEMBERS ELIGIBLE TO VOTE: 17
VOTE ON PANEL ACTION:
AFFIRMATIVE: 17