I notice that some room based fixed heaters do not have an on-off switch on them and also do not have a disconnect within sight.
It appears on my reading of article 424 that for one and two family dwellings you can use the branch circuit breaker (in the main panel) as the disconnect even if it is not within sight as long as the breaker allows for a "lockout".
Is this breaker having a potential for a "lockout" what keeps the manufacturers from having to provide an on/off or the electrician from putting an unsightly disconnect in the living room?
Are inspectors generally ok with this?