ceb58
Senior Member
- Location
- Raeford, NC
OK, help me out and dont beat me up too bad. I am doing some remodel work at a church. They have a baptismal built into the raised floor in the choir area. When they need to use it they have a removable floor cover they set to the side to use the pool. They want to have warm water in the pool and the plumber is installing a circulating pump/ heater. The pump will be located in a storage area behind the church. The pump/heater is 240v 30amp 1ph. Now looking through 680 I know I will have to comply with 680.21 A 1 as far as branch circ. to my disconnect. But what I am unclear on is. Will I have to install an emergency switch to comply with 680.41? And what about 680.26 B 1? The baptismal was "homemade" it is built from cinder block and is parged with mortar and sure-wall. Will the water need to be bonded? The piping is pvc so there is no way to bond the water through the plumbing.