At my house I have a 5 ton, 2 stage scroll compressor condensing unit, and my house lights blink on the unit starting.
Specs are 118 LRA, 230V, 23 FLA.
Lamps are incandescent 130 V.
Measurements at the unit disconnect switch are:
Normal Voltage 246 V
Starting Voltage: 231 V
Starting Amps: 121 A
Running Amps: 10 A (Low Stage)
Starting time: 1 second.
Start is on Low stage.
This is on a 1 year old house and has done this since installed.
There is no issue when the compressor goes from low stage to high stage.
Neutrals have all been checked, Meter, Panelboard, AC unit/disconnect, and are all tight.
If I place a hard start (start assist) kit (Capacitor and Start Relay) on the compressor, will it reduce the line current to the unit, so that my service doesn't see the full compressor start current? If so, any guess at how much less.