I have a building that whenever the chiller starts the lights blink, commputers without ups drop, and phones are sometimes lost. This occures only for a fraction of a second on start than all is ok. We placed a recorder on the main and the only thing of interest is the system voltage runs about 4 volts lower during the complete run time. We also did infered testing and everything looked ok. The trans. is a 500kva with paralled 350mcm al. 40 feet to meter, than 3 300mcm copper per phase to 800amp MDP about 10 feet. The building runs about 150amps without chiller than about 270amps with chiller running. Everything checks out ok, the only problem is for a fraction of second lights dim and a slight hum/vibration of main wires to MDP. thanks, john