Hold on ....
Mr Charlie b said 150mm2 cable (with ampacity 310A) and you said 400mm2 cable (with ampacity 420A) needed.
What's the differece?
I also said that I would use four conductors, and he said he would use three.Mr Charlie b said 150mm2 cable (with ampacity 310A) and you said 400mm2 cable (with ampacity 420A) needed.
I am not sure I can give you the best solution for your particular question. The closest "standard" overcurrent device setting (per the NEC) to your situation is 1200 amps. For a 1200 amp breaker, I would use four sets of 350 MCM conductors in parallel. That gives you a total ampacity of 1240 amps. The closest metric equivalent to 350 MCM is 150 mm2. So four sets of 150 mm2 might be your answer.
...And i didn't understand the meaning of length of run and this VD.
Voltage Drop (Phase to Phase), V/A.Km = 0.212
Impedance, Ohm / Km = 0.126
yes sure it is phase to phase, i have copied this text from the website of riyadh cable catalogue.
Voltage Drop (Phase to Phase), V/A.Km = 0.212
Impedance, Ohm / Km = 0.126
you cannot have a 3 phase breaker and only have 110v. It is 208V, 240V or possibly 480, etc.
To supply 1250 amps you would have to parallel conductors. How many parallel runs will you have. Also look at T. 310.15.
Also 1250 amps is not a standard size breaker. Where did you get this question from.
I interpret "medium voltage" as being above 600 volts, and below 25,000 volts. We are talking about voltages well below 600. So I don't understand your statement.this gentleman is not clear about his question.I think he is talking about Medium Voltage not Lv. . . .