Great. Then just measure the currents and phase angles and be done with it as it is just vector math after that.
I think its a bit more difficult than just vector math. As has been already pointed out, you need to solve 3 simultaneous equations with 3 unknowns.
However, I think there is a fourth unknown that hasn't been discussed. While it is known that the angles between the load current will be 120[FONT="]? [/FONT]apart, the angle
between the line and phase currents will also be unknown.
For instance, if we assign the angle θ to the load current from A-B, and θ-120 to the load current B-C and θ-240 to the load current C-A. And we then measure the line current to be Ia=102.38<0, Ib=110.48<-118.56, and Ic=108.96<-242.96. The vector equations for Ia=Iab-Ica, Ib=Ibc-Iab, and Ic=Ica-Ibc become:
Ia=(Iab*cos(θ)+jIab*sin(θ)) - (Ica*cos(θ-240)+jIca*sin(θ-240))
Ib=(Ibc*cos(θ-120)+jIbc*sin(θ-120)) - (Iab*cos(θ)+jIab*sin(θ))
Ic=(Ica*cos(θ-240)+jIca*sin(θ-240)) - (Ibc*cos(θ-120)+jIbc*sin(θ-120))
So even if you measure the line currents and their associated angles, you will need to solve 3 simultaneous equations with
4 unknowns (Iab, Ibc, Ica and θ) in order to determine the load currents.