√((Ia?+Ib?+Ic?)-(Ia*Ib)-(Ib*Ic)-(Ia*Ic))
How about you do it
√((Ia?+Ib?+Ic?)-(Ia*Ib)-(Ib*Ic)-(Ia*Ic))
How about you do it
Not resistive, but equal power factor, which is not the case in the OP.That formula won't cut it. It is based on purely resistive loading.
Not resistive, but equal power factor, which is not the case in the OP.
The neutral current is the vectorial sum of the phase currents.
No, it is based on purely resistive loading.Not resistive, but equal power factor, which is not the case in the OP.
The neutral current is the vectorial sum of the phase currents.
No, it is based on purely resistive loading.
Equal power-factor loading also works, but is provisional on the power factors all be leading or lagging, and not a combination of leading and lagging.
No, it is based on purely resistive loading.
Equal power-factor loading also works, but is provisional on the power factors all be leading or lagging, and not a combination of leading and lagging.
I have the perfect app for this, but it will not let me upload for some reason, it keeps saying invalid file
√((Ia?+Ib?+Ic?)-(Ia*Ib)-(Ib*Ic)-(Ia*Ic))
How about you do it
I'm curious where this formula came from. I know its suppose to provide an "approximation" of what neutral current will be.
The formula is exactly correct for a limited set of conditions. The formula is a useful approximation to the real world because in the real world we often end up pretty close to those conditions.
If you assume that there are no harmonics and that the three current phase angles are all 120 degrees apart, than this formula is exact. In a large system with reasonably balanced loading, or if you are calculating a small load such as a resistive heater where the elements are not evenly distributed on the phases, then the formula works.
In the example in the original post, the phase angles were wildly different than 120 degrees apart, so the formula gives a significantly incorrect result.
-Jon
Jon, thanks. It appears that people are just misapplying that formula, or making the assumption that it applies for all systems.
No one assumed, hence my other post and post #`12. Please read everything before posting
The loads of a 4-wire, 3-phase system are,
red to neutral current - 50A pf .707 lagging
yellow to neutral current - 40A pf .866 lagging
blue to neutral current - 40A pf .707 leading
determine the value of the current in the neutral wire
√((Ia?+Ib?+Ic?)-(Ia*Ib)-(Ib*Ic)-(Ia*Ic))
How about you do it
√((Ia?+Ib?+Ic?)-(Ia*Ib)-(Ib*Ic)-(Ia*Ic))
How about you do it
I did read everything.
Original Post.
Wrong equation for the problem. Gives a result of 10A, when actual answer is 58.86A.
Nice demonstration, but doesn't really help to determine the neutral current for the OP.
I've seen this neutral current equation quoted several times in recent posts, and in each case it was misapplied or based on assumptions.
Understood, but I felt as though the op was trying to get us to do a homework question, so I didn't bother reading closely enough, but once that was acknowledged, your post seemed arrogantly redundant.