Hi all,
I post a lot on the Photovoltaic Forum. I do not know much about air conditioner circuits.
I do vaguely remember in-rush current as a factor....:blink: I think :?
Can i downsize from the (E) 2p60 A brkr to a (N) 2p50A?
The A/C unit is a BRYANT,
208/230 VAC at a residence.
From the nameplate:
Compressor:
1 PH
60 HZ
26.4 RLA
134.0 LRA
Fan Motor:
1PH
60 HZ
26.4 RLA
1.5 FLA
Minimum Circuit Amps: 34.5
Max Fuse: 60 A
Max Ckt Brkr (*) 60
* HACR Type recommended
Any help is appreciated!