I was talking with another guy about the 'grounding being sized on the overcurrent device for the motors per NEC 250.122 (D)(1,2). The breaker is 70 amp. Instead of pulling a #8 copper based on table 250.122, it had an existing #10. He decided to pull in an ADDITIONAL #10 ground to help compensate for the size. This is one conduit, not parallel conduits.
Is it legal to do that?? It's my understanding it is not. You would have to size the single ground off of the overcurrent device, and not try to parallel them. Only thing I could find in the code was NEC 2008 250.122(F). But that even says that if you had parallel conduits then each ground pulled in each conduit would have to be sized to the over current device.
In theory I suppose if there is a fault, it would work. I know the NEC is suppose to be a permissive document, but I interpet this to not be permited.
Is it legal to do that?? It's my understanding it is not. You would have to size the single ground off of the overcurrent device, and not try to parallel them. Only thing I could find in the code was NEC 2008 250.122(F). But that even says that if you had parallel conduits then each ground pulled in each conduit would have to be sized to the over current device.
In theory I suppose if there is a fault, it would work. I know the NEC is suppose to be a permissive document, but I interpet this to not be permited.