It will all come down to the certifications, markings and how the location is actually classified.
If the equipment is certified and marked only to European Union standards (commonly called CENELEC), it is not acceptable in the US domestic market. See 506.9; read the entire Section.
Even if the equipment is properly marked per the NEC, unlike Class I, (See 501.5), there is no general provision for "cross application" of Zone equipment into Division classified locations. The location would need to be reclassified under 506.6(C). NOTE: this does not require the entire facility to be reclassified, only the general area around the Zone rated equipment. Some Division rated equipment is suitable for Zones though. See 506.9(C)(1).