I work for a pharmaceutical manufacturer and we are looking at making a product with a high amount of isopropyl alcohol (IPA). The basic layout is two rooms, one room for compounding the material and an adjacent room for filling the material, with a transfer pipe between.
In the compounding room there would be approximately 60 gallons of IPA. Given the low flash point (53 F) and the 60 gallons, I would classify it as a Class I, Division II location as most of the product will be in a covered tank and distributed through connected pipes. I am being asked what is the maximum amount of IPA we could have in that room without requiring explosion proof equipment? Does anyone know, is there an established threshold or volume for IPA to declassify it as a hazardous location? Or is there a calculation that can be done based on room size/air changes, etc? I looked on OSHA website for interpretations but couldn?t find anything.
The finished product would have 80% IPA. It would be transferred to the filling room via a teflon hose. In normal operations, the product would be enclosed in the filling room except at the filling area until the container is capped, about 30 seconds later. If this is the case, do you think the filling room would also need to have explosion proof equipment? or how would it be classified?
In the compounding room there would be approximately 60 gallons of IPA. Given the low flash point (53 F) and the 60 gallons, I would classify it as a Class I, Division II location as most of the product will be in a covered tank and distributed through connected pipes. I am being asked what is the maximum amount of IPA we could have in that room without requiring explosion proof equipment? Does anyone know, is there an established threshold or volume for IPA to declassify it as a hazardous location? Or is there a calculation that can be done based on room size/air changes, etc? I looked on OSHA website for interpretations but couldn?t find anything.
The finished product would have 80% IPA. It would be transferred to the filling room via a teflon hose. In normal operations, the product would be enclosed in the filling room except at the filling area until the container is capped, about 30 seconds later. If this is the case, do you think the filling room would also need to have explosion proof equipment? or how would it be classified?