cold water ground

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I should explain my last post. Table 310.15(B)(6) only applies when the service conductors or feeders carry the entire load of the house. When you have 2 disconnects then each service entrance cable does not serve the entire load simply because each does half-so to speak.
 
Status
Not open for further replies.
Top