Ron touched on something I would like to expand on in reference to running cables under the raised floor. Initially with the cables under the raised floor makes for a very clean room as none of the cables are visible. However the real purpose of the raised floor is to be used for a plenum for positive pressure HVAC distribution.
Equipment installers are very lazy when it comes to running cables, and have no plans on cable routing, and spend even less time dressing them if they don?t have too. Running under the floor just gives them the excuse to be sloppy. The processing equipment requires a lot of cabling, and over time as the room is filled up, the area beneath the raised floor becomes very congested and will block the air flow causing hot spots through out the room. Now couple that with cable mining, it is not possible with the chaotic install method when ran under the floor.
The real solution is an engineered structured cabling system complying with Bellcore Network Equipment Building Systems (NEBS). This evolves installing multi level cable racks and raceways to facilitate the various cable groups used. This typically includes three ladder type cable racks or optical troughs installed centered above and running parallel to the equipment line-ups segregated by signal type (alarm, telemetry, signal, optical, dc power, and ground). Further more installation practices should be put into place and strictly enforced as to how and where cables are installed. Basically the cables have to be formed and laced in such a manner you can place your finger on the cable and run it along the entire length of the route with out any cross-overs, twist, or divers.