Hello,
My name is Joey Barnett and I am prepping for my exam. I have a test question that I am confused about. I have a different answer than what the instructor has given me. This is based on Article 445.14 The question is:
Live parts of generators operated at MORE than _____ to ground shall not be exposed to accidental contact where accessible to unqualified persons.
1. 50v
2. 120v
3. 150v
4. All the above
The article is identical to the question and states 50v, the instructors answer is all the above. I know that 120v and 150v shall not be exposed but the way the question is worded I believe the answer should be 50v because it states MORE than vs which of the answers below constitute to the NEC.
Thank you for your assistance.
JB