I do not understand why it is required to do this at every single service disconnect (as in, what is the real life consequence in only doing it at one of the disconnects?), but somehow that is the way the code ended up being written.
The Main Bonding Jumper at each disconnect in a Service with multiple switches is needed because the jumper at each switch is sized for the Service Entrance Conductors that feed the switch. This becomes more applicable with larger switches and you size a wire bonding jumper according to the SE conductors feeding that switch.
If you were to install the bond at only 1 of the Service Disconnect Switches in a multiple separate switch service, it may be undersized the other switches. If there were a fault in multiple switches at the same time, the bonding jumper would be undersized for the fault incident. Also what if the only switch with the bonding jumper were removed...it would leave the others un-bonded.
It is important to bond at each Service Disconnecting Means to provide the low-impedance ground fault path back to the source with a bonding jumper correctly sized for the possible available fault current at that individual switch.