Here's the situation: a detached garage with only a 12g 110V supply line running under a lot of concrete (big $$ to change service). The owner got an EV and would like to have 220V/20A to plug the car in for faster charging. The wiring in the garage is old and not up to current code (no GFCI for example). Here is my proposed solution:
1) Install a new double pole 20A breaker in panel at house and move this circuit to that breaker, thus providing 220V without neutral to garage. Label the white wire as "hot".
2) In order to provide 110V power in garage, install a properly sized 220->110 isolation transformer in the garage in parallel with the 220V outlet for the EV only.
3 Since the 110V output is floating that is not ideal since neither side is neutral. I propose to ground one side of the output and then use a GFCI breaker after this point.
I believe this is safe and would not allow current to flow through ground without tripping the GFCI. It is probably safer than the existing conditions. I cannot find any relevant threads on this topic. Any pointers or comments?
1) Install a new double pole 20A breaker in panel at house and move this circuit to that breaker, thus providing 220V without neutral to garage. Label the white wire as "hot".
2) In order to provide 110V power in garage, install a properly sized 220->110 isolation transformer in the garage in parallel with the 220V outlet for the EV only.
3 Since the 110V output is floating that is not ideal since neither side is neutral. I propose to ground one side of the output and then use a GFCI breaker after this point.
I believe this is safe and would not allow current to flow through ground without tripping the GFCI. It is probably safer than the existing conditions. I cannot find any relevant threads on this topic. Any pointers or comments?