Could Negative Sequence be causing my motor problems?
I have a project I am working on in Missouri with a city water department.
The water utility just finished replacing an old 150 HP motor and pump with a new 150 HP motor and pump.
The new pump on this motor is configured to be nonoverloading, meaning it will never pull more than 140 HP.
The reason I was called is the motor is drawing more power than it should and tripping the old 150 HP soft-start.
The electrician working on the project told the city the soft-starter was bad and needed to be replaced.
The water department manager questioned this, as the soft-starter was working fine with the old motor and is only 5 years old.
I have confirmed with flow tests and pump curves that the correct pump and impeller are installed and thus the pump is a true nonoverloading pump.
I have also confirmed that the soft-starter is functioning correctly.
The soft-start goes through a 60-second ramp up during starting and a 60-second ramp down when stopping.
After the 60-second ramp up the starter goes into a bypass mode, where the SCR?s are bypassed and the motor continues to run off straight power.
To make a long story short the starter is protecting the motor just as it was designed to do.
The motor has the following name plate rating (460 V, 164.0 FLA, 1.15 SF, 94.5 NEMA Efficiency, 90.8 NOM PF, 3555 RPM)
Voltage prior to start up
A ? B = 484v
B ? C = 488v
C ? A = 488v
The readings I have been getting, as measured on the motor leads (after the soft-start is bypassed and motor is at full rpms) with a RMS digital meter are the following:
Running Voltage
A ? B = 476v
B ? C = 482v
C ? A = 483v
Running Current
A = 184amps
B = 195amps
C = 199amps
The Voltage reading seems to be normal to me. There is a slight imbalance between phase voltages and a slight voltage drop at startup but I would consider both of these to be normal, or at least within normal limits.
Here is what I am unable to explain.
I don?t understand why the full load running amps are much greater than the name plate rating. The motor is running well beyond even the service factor.
With the pump and present flow rates the motor should be running around 130 HP not 183 HP (which is what I calculate).
I just cannot believe that this new motor could be bad yet still operate this close to its design ratings.
I?ve used a megger to check the motor and the windings test out that there are no shorts.
I have also checked all of the leads and all are connected correctly.
Could the motor have been manufactured with the incorrect number of windings or some other flaw to through off the name plate information?
My only other thought besides a bad motor is that there could be a problem with the incoming power, but I don?t even know what to look for.
Could my problem possibly be a phase shift on the incoming service such that the three phase voltages are no longer 120 out of phase (negative sequencing)?
One of the water utility employees said he worked on a submersible well pump many years ago that kept burning out.
The symptoms were similar in that they had voltage on all three phases yet were also drawing more amps than the nameplate.
They replaced the pump three times, each time with the motor burning out.
Finally, the problem was narrowed down to the power transformer.
The transformer was replaced and the problem was fixed.
He could not remember what the problem was with the transformer.
Do you know of any problems besides phase loss in a transformer that could cause a motor to burn out or operate above nameplate ratings?
The service is fed from a pad mounted 3-phase transformer that is fed from a 3-phase overhead line. I?m not sure where the substation is (near or far) in relation to this site and I do not know if there are any cap banks on the line.
I am at a loss to explain this and have run out of ideas on what to test or measuer. Any ideas or explanations of similar experiences would be greatly appreciated.
Thanks again.
Jim
{Moderator's Note: Edited to remove personal contact information. If you wish to contact this person, please send a Private Message.}
[ July 11, 2005, 08:31 AM: Message edited by: charlie b ]
A ? B = 484v
B ? C = 488v
C ? A = 488v
Running Voltage
A ? B = 476v
B ? C = 482v
C ? A = 483v
Running Current
A = 184amps
B = 195amps
C = 199amps
Thanks again.
Jim