I had a whole house inspector put in his report that the second floor receptacles were grounded to a cold water copper line and that was not to code. I like to prove whole house inspector wrong so I searched for about 3 hours for anything about this in the NEC. I was hoping somebody else found it.
I'm pretty sure that once was an acceptable way of getting a ground to something that was once ungrounded. I think it was about 1990 or 1993 NEC that no longer permitted this.
I'm wondering why they don't leave the piping completely out of the electrical system. Seems stupid.
Get the ground from rods, ufer, plates or something besides the piping system.
I think that would create more problems than is solves. Why do we need equipotential grounding grids in certain places? Because conductive objects in contact with earth are the point where voltage potential between "earthed" objects and the grounded/grounding conductors of the electrical system will be at dangerous levels at times. Bonding them all together ensures they are all at same potential.
You will still have potential to the piping - especially if a portion of the piping us buried in the earth. Makes more sense to insure it is bonded to electrical system rather than allow it to introduce voltage potential.
Would make more sense to stop using grounded conductors as current carrying conductors, then you have no voltage drop on the current carrying portions that will result in a voltage between a current carrying conductor and a non current carrying object.
Anyone having trouble getting to page 2 of this thread? When I click on "go to first new post" it goes to the beginning or #1 post. I even clicked on page 2 and last post and still returns to post #1.
Edit: After I posted, it then went to the 2nd page, and there was already 1 post there. Very strange!
I did not have trouble with this thread but have occasionally the past few weeks had similar problems from time to time. Always brings me to post#1 and will not let me go to any other page in that particular thread when it does happen.