current phase angles shifted 30deg from voltage angles

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
... Now here's the question: is the L-L current leading or lagging the L-N voltage, since that would make the difference between 90+30=120 or 90-30=60deg?
Depends on which line you reference your L-L voltage. If the reference is the lagging line?such as Vab, Vbc, Vca?then a 90? L-L current lag is a 60? L-N current lag, or a 90? L-L current lead is a 120? L-N current lead.

Reference your voltage the other way?Vac, Vba, Vcb?and 90? L-L lag is 120? L-N lag, while a 90? L-L current lead would be 60? L-N current lead.

You have to take this into consideration where L-L current leads and lags combine through a common line, as the two voltages are referenced to their respective uncommon lines.
 

skeshesh

Senior Member
Location
Los Angeles, Ca
Depends on which line you reference your L-L voltage. If the reference is the lagging line?such as Vab, Vbc, Vca?then a 90? L-L current lag is a 60? L-N current lag, or a 90? L-L current lead is a 120? L-N current lead.

Reference your voltage the other way?Vac, Vba, Vcb?and 90? L-L lag is 120? L-N lag, while a 90? L-L current lead would be 60? L-N current lead.

You have to take this into consideration where L-L current leads and lags combine through a common line, as the two voltages are referenced to their respective uncommon lines.

Yup, agreed. Now should we talk about the system with the added consideration of p.f.?
 

skeshesh

Senior Member
Location
Los Angeles, Ca
I don't believe anyone will stop you :D

However, my foremost concern is mull' having an understanding of his reason for posting...

hehe true :roll: Maybe tomorrow... I'm gonno go try to stop my brain from thinking about electricity by drowning it in the silly filth our media calls entertainment and dream of a golden brown turkey!
 