690.4(B) says that PV Source or Output circuits shall not be installed in the same raceway, etc.........of other systems.
My question is this: I have an installer with a ground mount system. It has 2 separate racks, separated by approx 20 ft. He only installed (1) conduit between the racks and needs to get an AC feed to an inverter as well as a PV Source Circuit in this conduit. (3" PVC installed underground). Seeing that the inverter output circuit is still part of the "PV System", is this permissible to install the AC and DC circuits together in this conduit?
:?
Thanks!
My question is this: I have an installer with a ground mount system. It has 2 separate racks, separated by approx 20 ft. He only installed (1) conduit between the racks and needs to get an AC feed to an inverter as well as a PV Source Circuit in this conduit. (3" PVC installed underground). Seeing that the inverter output circuit is still part of the "PV System", is this permissible to install the AC and DC circuits together in this conduit?
:?