Article 240.21(C)(3)
Typically I stay within the 10' rule in 240.21(C)(2), but what is to stop me from going 25' before the OCPD for transformer secondary conductors in a non-dwelling unit, maybe a commercial building?
There doesn't appear to be a definition of industrial installation. The International Building Code includes most industrial occupancies within the Group B definition.
What kind of experiences have you folks had when going past 10' with the secondary conductors in a commercial building that has Maintenance Personnel (not electricians)?