You right. This is from the 05
(2) Grounded Conductor
Where (1) an equipment
grounding conductor is not run with the supply to the building or structure, (2) there are no continuous metallic paths
bonded to the grounding system in each building or structure
involved, and (3) ground-fault protection of equipment has not been installed on the supply side of the feeder(s), [COLOR="MediumTurquoise"]the
grounded conductor run with the supply to the building or
structure shall be connected to the building or structure
disconnecting means and to the grounding electrode(s) and
shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded[/COLOR].