AESolutions
Member
ok here is what i have....its a Carrier pkg unti model 50TM-008-A-601, which is a 480v 3phase, it has two compressors each have a RLA of 6.4 and a LRA of 42, also there are (2) fans which are 1/4 Hp .7 FLA and the IFM FLA is 2.6, it also has heat strips (model#CRHEATER016A00), 13.9 Kw, 16.7 FLA. the table I have for the entire unit says that the MCA should be 24.1 with an overcurrent protection of 25. for disconnect size it says the FLA is 22 and LRA is 108...I'm lost, motors are not my thing, usually pkg have two hookups, this is a single point hookup.