Duct Bank & Manhole Entry

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
So my conduits have to be 21"-24" deep. The manhole econduit entry window is about 16"-18" from grade. WOuld an offset be required or couls the conduit be run on angle to makeup the few inch difference?



1713442694648.png 1713442628979.png
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
What is telling you that the entry is that far above grade? It appears to me that it is only 1.5 to 2" above grade.
 