Ductless Mini Splits AC Interconnect Wiring....

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
TC is a good solution, its sunlight resistant, DB rated and stranded so easy to work with.

And only permitted to be used in a raceway or cable tray in most applications, especially applications where these mini AC systems would be placed.

If you need to use a raceway anyway why bother purchasing TC?

I would think an MC cable designed for wet location would be the thing for an HVAC guy to stock for this application. Something that will work both indoors and out and in almost any occupancy/construction type.

I have never seen any but 330.10(A)(11) suggests there is such a thing.
 