If going from a 4-0 riser to a 200a fused disconnect, to meter sockets, to disconnects shouldn't 4 conductors be run from the first 200a disco?
If going from a 4-0 riser to a 200a fused disconnect, to meter sockets, to disconnects shouldn't 4 conductors be run from the first 200a disco?
Not a POCO standard around here. Just the way the electrician wants to do it.Is the first disconnect a poco requirement? By the NEC yes, 4 conductors.but since you're in front of the meter sockets it may be a poco standard. Ask them.
Does the 200 amp disconnect qualify as the service disconnect or is it a meter disconnecting means as mentioned in 230.82(3)?
The POCO would allow it, but I was thinking the same thing about the meter can.where are you going to get a meter can that has an isolated neutral and would POCO rules allow this.