What code year was it required to install fan rated boxes in every bedroom that had an over head light even if a light was hung instead? Thank You.
That is a code change for 2011. 314.27 (C) It says to the effect if you have a ceiling box that has more than one switch leg in it then the box must be rated for a fan.
That is correct. Not sure why anyone would run a 3 wire cable to a ceiling box and not install a fan box..
If the print shows fan you put a fan rated box. If it shows light, you put a standard box. That is if your pinching pennys. I always put a fan rated box.
That is correct. Not sure why anyone would run a 3 wire cable to a ceiling box and not install a fan box..
....also not sure why the NEC would make this change, and not just flat out require all ceiling boxes be fan rated. Does a fan/light combo installed on a box, with just a hot and a neutral have a different effect, or is it the weight of the additional conductor (second sw leg) that made the CMP change this? IMO, if a change was made, they should have required all ceiling boxes to be fan rated (in rooms normally supplied with them), and not rely on the amount of conductors in the box.
....also not sure why the NEC would make this change, and not just flat out require all ceiling boxes be fan rated. Does a fan/light combo installed on a box, with just a hot and a neutral have a different effect, or is it the weight of the additional conductor (second sw leg) that made the CMP change this? IMO, if a change was made, they should have required all ceiling boxes to be fan rated (in rooms normally supplied with them), and not rely on the amount of conductors in the box.
The MA amendments had wording to this effect back in 05. I believe it was if there was six square feet or more of ceiling space and it had a light then the box had to be rated.
It was deleted in our in the 08 amendments though.
That is correct. Not sure why anyone would run a 3 wire cable to a ceiling box and not install a fan box..
I know why a 3 cable conductor is better for a ceiling box, but is the main reason, for a 3-way switch, or control of the light and fan independently, or speed control of the fan why a 3 cable is run in new construction?
So then I explained the difference was not so much the weight, but the fact that the fan was a dynamic load and a light was a static load and the different stresses required different mounting hardware.
That he understood.
It is for independent control of fan & light. Today with so many high end fans that have their own electronic wall switch there is almost no need for a 3 wire. Personally I like having the option for a wall speed control and a wall switch for the light.
I find that if I use multi-syllable words when explaining something they seem to 'understand' too.