Lets' see , I've got 4250 watts of fixed heat divided by 240v = 17.7 amps x 1.25 for continuous load = 22.13 amps ,. Lets call it 23 amps . 12\2 nmb is good for 25 amps @ 60 deg. there will be no insulation my question is can I use a 20amp breaker on this circuit? it should never see more than 18. amps ? the wire is good for 25 .
Also I live in Massachusetts where we have this:
I will most likely run 2 circuits.
So I guess the question is. Can the over-current device be based on 18 amps(100%) while the conductor ampacity gets based on the full load plus 125% Sitting here,. without the good book,.. I'd say no . but I'm not sure why it would ever be a problem?
Also I live in Massachusetts where we have this:
Again there will be no thermal insulation.334.80 Ampacity. Type NM, NMC, and NMS cable shall have conductors rated at 90?C
(194?F).
Where installed in thermal insulation, the ampacity of conductors shall be that of 60?C
(140?F) conductors. The ampacity of Types NM, NMC, and NMS cable installed in cable tray
shall be determined in accordance with 392.11.
I will most likely run 2 circuits.
So I guess the question is. Can the over-current device be based on 18 amps(100%) while the conductor ampacity gets based on the full load plus 125% Sitting here,. without the good book,.. I'd say no . but I'm not sure why it would ever be a problem?